DM's build doesn't have any room for such expansion so the online sizing table linked below (also recommended by Thailand's electrical guru), serves to bolster the handy "Aussie rules" wire-sizing chart posted earlier. If you select single-phase, 45 A (for the PEA meter rating), a 10 m run to cover DM's best guesstimate and "conduit on a wall or trunking" (like at DM's new place), it offers 10mm.
https://www.doncastercables.com/technical-help/
Ruling out aluminium because it can be more trouble than it is worth (and the PEA probably wouldn't touch it), the 10mm copper that his builder suggests (and also works for BD) would be the acceptable minimum. Personally (based on personal experience) and in alignment with a few fellow members here, the 16mm copper would be the optimum gauge, just in case DM gets that karaoke machine or wants to provide power for the yacht when it's moored at the jetty out back.
Based on a guess. Do you base where oil and gas is on a guess or do you do take more scientific approach. Completely wrong about PEA and AL cable as well. What does your C&G's tell you about Jons actual load requirements or would it not be better to ask Jon?